Overview
38 S1A53838 09/2011
Common control schemes
2-wire control
1. Wire the logic inputs as indicated in the above figure.
2. Set switch SW102 to source.
3. Program common parameters of ATV212 (see Quick Menu page 55
).
4. Program specific parameters for 2-wire control as indicated in the following table:
Note: If F111 and F112 are switched simultaneously, the drive will go at 0 speed.
DANGER
HAZARD OF ELECTRIC SHOCK, EXPLOSION OR ARC FLASH
Read and understand the instructions in "before you begin" chapter, before performing the procedure in this
section.
Failure to follow these instructions will result in death or serious injury.
DANGER
UNINTENDED EQUIPMENT OPERATION
z To modify the setting of the switches, the product must be switched off.
z Do not change the setting of switch SW102 unless your system is properly wired.
Failure to follow these instructions will result in death or serious injury.
R/L1
S/L2
T/L3
U/T1
V/T2
W/T3
FLC
FLB
FLA
PP
PA/+PO
PC/-
SCR
A
GND
B
RUN
PRG
MON
%
Hz
MODE
Loc
Rem
ENT
RUN STOP
M
RYA
RYC
FM
F
R
RES
PLC
P24
CC
Sink
PLC
FM
Source
SW102
IU
SW101
Term
SW103
VIA U
VIB U
I
PTC
SW100
CC
VIA
VIB
Run forward
Run reverse
Parameter Page Setting Factory value
CMOd [Command mode sel] 77
0 [Logic inputs] 0
F111 [LI F selection] 90
2 [forward] 2
F112 [LI R selection]
90
3 [reverse] 6