Remote Mode
When the ATV212 drive is in the remote mode, the LOC/REM LED is off.
Starting and Stopping the Motor in Remote Mode
The diagram on page 46 illustrates the start/stop command source when the drive is in remote mode.
With Logic Input Terminals
Use the logic input terminals F, R, RES, or VIA to start the drive if parameter [Command mode sel] (CMOd) is
set to [Logic Inputs] (0) (factory setting).
With the display terminals
The drive responds to commands from the embedded display terminal or graphic display option, just as in local
mode, if parameter [Command mode sel] (CMOd) is set to [HMI] (1).
With Serial Communication
The drive responds to commands sent over the serial communication link (Modbus
®
, Metasys
®
N2, Apogee
®
FLN, BACnet or LonWorks
®
) if parameter [Command mode sel] (CMOd) is set to [Communication] (2).
The drive responds to commands sent over the RJ45 communication port if parameter [Com channel choice]
(F807) is set to 0. Other protocols are available when F807 is set to 1 on open style port.
With the graphic/embeded display terminals STOP Key
The graphic/embeded display terminals STOP key is active when the drive is in remote mode. Pressing the
STOP key causes the drive to stop according to the setting of parameters [Ext. fault stop Mode] (F603), [DC
brk time ext flt] (F604), and [DC braking current] (F251) (see page 115
and page 88) . After the drive has
come to a stop, the graphic/embeded display terminals display E and the fault relay is activated.
Adjusting the Motor Speed in Remote Mode
The diagram on page 46
illustrates the speed reference source when the drive is in remote mode.
By Analog Input VIA
A 0–10 Vdc or 4–20 mA signal connected to VIA and CC can be used to adjust the motor speed if:
z Parameter [Frequency mode sel] (FMOd) is set to 1 (factory setting).
z Alternate speed reference source parameter [Remote spd ref 2] (F207) has not been enabled (see page
78
).
The analog signal type depends on the setting of switch SW100 and parameters F109, F201F204, and
F470F471.
By Analog Input VIB
A 0–10 Vdc signal connected to VIB and CC can be used to adjust the motor speed if:
z Parameter [Frequency mode sel] (FMOd) is set to 2.
z Alternate speed reference source parameter [Remote spd ref 2] (F207) has not been enabled.
The control that VIB has over motor speed depends on the setting of switch SW100 and parameters F210
F213, F472F473, and F645.