I/O Control Parameters
102 S1A53838 09/2011
36 [Fault relay]
(The drive is not in a fault state during
auto clear detected fault attempts.
See also function 10 page 98
)
WARNING
LOSS OF CONTROL
z When F130, F132, F137 is set to 36, the output will be active
when the drive will detect a fault.
z The drive status will not be detected if the wiring is damaged for any
reason.
z Do not select 36 unless you are sure that your signal will be present
in any case.
Failure to follow these instructions can result in death, serious inju-
ry, or equipment damage.
OFF: No drive detected fault
ON: drive detected
fault.
Relay activates when a clearable fault occurs and the drive attempts to re-
start. Relay deactivates when drive is restarting.
37 [Inv fault relay]
Inversion of Fault relay function 36
OFF: drive detected
fault
ON: No drive detected fault
Relay deactivates when a clearable fault occurs and the drive attempts to
restart. Relay activates when drive is restarting.
38 [Ser. data relay FL]
Serial communication data
OFF: Serial communication word FA50 bit 0 = 0
ON: Serial communication word FA50 bit 0 = 1
39 [Inv ser. dat rel. FL]
Inversion of ser. dat rel. FL function
OFF: Serial communication word FA50 bit 0 = 1
ON: Serial communication word FA50 bit 0 = 0
40 [Ser. data relay RY]
Serial communication data
OFF: Serial communication word FA50 bit 1 = 0
ON: Serial communication word FA50 bit 1 = 1
41 [Inv ser. dat rel RY]
Inversion of ser. dat rel. RY function
OFF: Serial communication word FA50 bit 1 = 1
ON: Serial communication word FA50 bit 1 = 0
42 [Drive run time al]
Drive operational run time alarm
(see page 120
for more detail on
parameter F621).
OFF: Run time is < F621 time setting
ON: Run time is F621 time setting
43 [Inv.drive run time al] Inversion of Drive
run time al function
OFF: Run time is F621 time setting
ON: Run time is < F621 time setting
44
[D
rive serv. alarm]
Drive service alarm (see page 133
for more detail on parameter
F634).
OFF: drive maintenance detected fault not active
ON: drive maintenance detected fault active
45
[Inv. d
rive serv. alarm] Inversion of
Drive serv. alarm function
OFF: drive maintenance detected fault active
ON: drive maintenance detected fault not active
48 [LI F state]
Logic input F state
OFF: Logic input F is not active
ON: Logic input F is active
49
[Inv. LI F state
] Inversion of LI F state
function
OFF: Logic input F is active
ON: Logic input F is not active
50 [LI R state]
Logic input R state
OFF: Logic input R is not active
ON: Logic input R is active
51
[Inv. LI R state
] Inversion of LI R state
function
OFF: Logic input R is active
ON: Logic input R is not active
52 [Speed ref = VIA]
Drive speed reference equals VIA sig-
nal
OFF: Speed reference from the source identified by
[Frequency mode sel] (FMOd) or the source identified by
[Remote spd ref 2] (F207) VIA signal
ON: Speed reference from the source identified by FMOd or the source
identified by F207 = VIA signal
53 [Inv. speed ref = VIA] Inversion of
Speed ref = VIA function
OFF: Speed reference from the source identified by
[Frequency mode sel] (FMOd) or the source identified by
[Remote spd ref 2] (F207) = VIA signal
ON: Speed reference from the source identified by FMOd or the source
identified by F207 VIA signal
Function No. / Description Action